480sparky said:Should be no problem as long as the dimmer is on the load side of the protection.
infinity said:How would being on the line side affect the dimmer?
If it is a problem remove the fixture from the GFCI altogether.
LumenArch said:Is it possible to dim a light fixture on a GFCI / GFI circuit?
Will the GFCI trip as soon as the light is dimmed? This is for the installation of a fixture in a shower. Any recommendations?
Thanks.
georgestolz said:That's a really good question. In the 2008 cycle, it was brought to one of the CMP's attention that some dimmers use the ground as a neutral from the factory, in case there is no neutral available at the switch. Thanks to a lack of a 2/3's agreement one way or the other, neutrals are still not required to be included at switch locations per 404.2(A), exception.
I imagine if one of those dimmers were installed on the load side of a GFCI, then the GFCI might trip.