Re: Dimming Duplex Receptacles

General purpose dimmer switches are only permitted to be connected to permanently installed luminaires per section 404.14(E).

Your description of a "dimmer panel" makes me think you are refering to a "dimmer rack" used for theater lighting. I don't see anything in that section that permits receptacles to be controlled by dimming fiunctions. See Article 520.
 
Re: Dimming Duplex Receptacles

404.14 (E) Dimmer Switches. General-use dimmer switches shall be used only to control permanently installed incandescent luminaires (lighting fixtures) unless listed for the control of other loads and installed accordingly.
 
Re: Dimming Duplex Receptacles

404.14 (E) Dimmer Switches. General-use dimmer switches shall be used only to control permanently installed incandescent luminaires (lighting fixtures) unless listed for the control of other loads and installed accordingly.
 
Re: Dimming Duplex Receptacles

In the 2002 NEC Art.404.14(E) States that dimmer switches shall only be used on permanently installed light fixtures.
 
Re: Dimming Duplex Receptacles

Did you say dimming panel? I am going out on a limb here but I believe that theatrical dimming panels often are used for switching functions also. I believe they use a communication protocol called DMX to switch loads and run motors (to lower or raise devices above the stage) and move lighting.

That being said, I think DMX is a communication protocol not a power distribution system. It may be able to activate a relay or tell a switching panel to energize an outlet. In other words, I think a theatrical dimming panel can control a 125V, 20A outlet but I don't think It can directly power it.

However, maybe someone sells a dimming panel with a switching card built into it. It would be like a discrete output relay card in a PLC. You would wire from the breaker to the dimmer relay card to the outlet. If you were standing at the outlet, it would look like the dimmer panel was suppling the outlet. Cool thing is that the guy in the control booth could switch loads around the stage in concert with the lighting.

So in the course of answering a simple question I have gone from "Yes you can", to "No you can't", back to "Yes you can". Thats what happens when type before you think. ;)
 
Re: Dimming Duplex Receptacles

If it is a dimmer panel, does 404.14(E) apply? I don't think that a theater dimming system is a "general use dimmer switch".
Don
 
Re: Dimming Duplex Receptacles

the dimmer pannel that you are refering to absolutely can not operate recepticles. Rating of recepticles has nothing to do with it. If after you have collected all your info & still proceed you might get it past an inspector if he doesnt know what he's looking at. THINK about the outcome if you do hook this up ask yourself was it worth it
 
Re: Dimming Duplex Receptacles

You could end up paying for damage electronics or equipment.You been warned and told why so your on your own if you still do it
 
Re: Dimming Duplex Receptacles

Electronics Diversified Inc makes dimmer sticks with receptacles on them. They look like a standard configuration. I don't see a UL listing on the cut sheet, but my guess is that this may be allowed for protable stage lighting.

(I am assuming we are talking about stage lighting) The people who set these up usually know what they are doing. And the dimmer outlets would usually be hung above a stage. It isn't too likely that someone would plug a computer or toaster into one.
 
Re: Dimming Duplex Receptacles

After reading and responding to this post, I got a call from My Father who was having a problem at his new condo. Went over and found the receptacle near the bed had been wired to a wall box dimmer. I'll bet every unit in the building is like that. I told him don't plug anything other than a lamp into that receptacle - no alarm clock, TV, vacuum etc. Well now I know of a great place to test the effects of voltage drop on equipment.

Also found 4 ceiling fans wired to the unswitched hot. Electrician guessed which hot in the box to use and guessed wrong each time. He never tried the switches to see if they did anything. Nice huh.
 
Re: Dimming Duplex Receptacles

Originally posted by sceepe:
Went over and found the receptacle near the bed had been wired to a wall box dimmer.

Also found 4 ceiling fans wired to the unswitched hot.
Uh, if this was in the same room, I'd say the receptacle could be feeding the switch, which is supposed to be dimming the lights on the ceiling fan. Perhaps? :D
 
Re: Dimming Duplex Receptacles

I'd say the receptacle could be feeding the switch, which is supposed to be dimming the lights on the ceiling fan. Perhaps
That might be what they had in mind but didn't get hooked up that way. Slide the dimmer and watch the lamp plugged into the outlet dimm. Didn't try it with the TV but I wonder what would happen.
 