180718-2111 EDT
keith gigabyte:
Some key points.
1. You were told there was no major light flickering before the work you did was done. If true, might be suspect, then most likely some connection you made that is common to the washer, or something you did not do but but was affected by some wires you may have moved somewhat is where to look for a bad connection.
2. What is flicker? I can see an incandescent flicker with as little as 2 % change in voltage, but I have to be looking closely, sort of know when to look. From peripheral vision I probably would not notice. I would expect more like 5 to 10 % change for an average customer to detect flicker. At 120 V this is in the range of 6 to 12 V change at the bulb.
You need to make measurements.
What exactly did you replace?
You need a good meter with a resolution of 0.1 V on a range that reads 120 V. You may need something with fast response. However, if you use a 1500 W space heater to provide a load change from 0 to about 10 A, then you can control the on-off timing.
Two 7.5 W incandescent bulbs also can be useful as qualitative voltage detectors, one on each phase.
Measure voltage change directly on the wires, not the terminating lug, at the inpit to the main breaker. Do line to line, each line to neutral, and neutral to a screwdriver in outside earth. If large changes occur, then there is at least a problem before the main breaker.
Do the same tests on the panel bus bars.
If everything is good at this point, then move on to the washer branch circuit and anything common to it.
.