I have a customer that recently changed the outdoor condenser and every time the condenser kik's on the lights are dimming for the split second and he hears that the wire is shaking inside the EMT.
I checked for lose connection but could not locate nothing wrong .
The unit feed with # 6 conductor(50 Amp breaker) and before it lives the house it spliced to # 8 UF conductor . The name plate is reading 29 Amp at 230 V.
I was reading 35 Amp at start up and 9 Amp running current.
The main feeder to the house is 200 Amp with 3/0 wire no lose connection there.
Any ideas?
I checked for lose connection but could not locate nothing wrong .
The unit feed with # 6 conductor(50 Amp breaker) and before it lives the house it spliced to # 8 UF conductor . The name plate is reading 29 Amp at 230 V.
I was reading 35 Amp at start up and 9 Amp running current.
The main feeder to the house is 200 Amp with 3/0 wire no lose connection there.
Any ideas?