Dimming line side of GFCI
chris kennedy said:
What would happen? I see nothing in the Hubbell instructions that says you cant.
You cannot dim a receptacle unless it is an approved dimming recep. That info is on the dimmer installation. But you knew that-- Are you just being curious?
Our guys did it yesterday after callin Lutron and it works. I'm reading P@S now.
Here is what Lutron sells to dim a recep. You need a special plug for this device
Thanks Dennis, I am aware of the proper way to dim a receptacle. Please have some coffee and read post one again.:grin:
Okay-- now I'm mad. :D Coffee makes me crazy- you sure you want me to have some... GTG later.
Why would Hubbell include this information in the instructions when dimming a receptacle is already prohibited by 404.14(E)?
For guys like we have here?:mad: Then again , I bet they never read GFCI instructions either.
you guys keep talking about not being able to dim a receptacle, yet the OP never once mentioned a receptacle. Perhaps he is looking to feed a deadfront GFFI with a dimmer for an underwater light or something.
To answer the OP question, no you cannot feed a conventional GFI from a dimmer. The GFI is expecting clean 120v on its input. The chopped up waveform from a dimmer will either fry the GFI or cause it to not work properly. Leviton or Hubbell or someone makes a GFI designed for dimming use where the device has 2 sets of inputs. One is 120v power to operate the GFI and the second is the input from the dimmer which is passed to the output terminals.
To add GFCI protection to a dimmed source you need a Levington 36895 GFCI. Its expensive ($90 for a GFCI!!) and YELLOW!!! but it is the right tool for the job.
You cant use a normal GFCI after a dimmer because the GFCI electronics require the fullline voltage to operate, and after a dimmer the line is chopped up by the dimmer's triac.
I ran into this a couple months ago.
The guy who roughed in a bathroom ran the switch to a gfci and then up to a light. No problem until they wanted the light dimmed.. ofcourse. So then I thought- oh hey no problem- faceless GFCI - and we're set. Nope. GFCI won't trip on a dimmed source.
So I messed around for an hour fishing in extra wires around to make the system work properly - aka- gfci before the dimmer.