Dimming Panel 0-10v

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ

Attachments

  • Capture.jpg
    Capture.jpg
    10.5 KB · Views: 0
  • Capture 2.jpg
    Capture 2.jpg
    21.5 KB · Views: 0

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Just because that cable is constructed with line voltage and CL2 doesn't give you permission to pull both in your own conduit- if that's what you are asking.

-Hal
 

follybeacher

Member
Location
USA
Occupation
Estimator

What he's saying is just because Southwire makes MC cable that combines 0-10LV wire with 600V wire doesn't mean you can route your individual conductors in a single raceway. You need to route the 0-10LV cables exterior to your line voltage raceway (NEC 300.3)
 

mstrlucky74

Senior Member
Location
NJ
What he's saying is just because Southwire makes MC cable that combines 0-10LV wire with 600V wire doesn't mean you can route your individual conductors in a single raceway. You need to route the 0-10LV cables exterior to your line voltage raceway (NEC 300.3)

That's weird how they can be under one armor but not in one conduit.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Haven't we talked about this subject here literally 1000 times? Several of those threads YOU were part of and even started???

I'm beginning to think that other people in your department all come here to ask questions under the same sign-in.

-Hal
 
Last edited:

mstrlucky74

Senior Member
Location
NJ
Haven't we talked about this subject here literally 1000 times? Several of those threads YOU were part of and even started???

I'm beginning to think that other people in your department all come here to ask questions under the same sign-in.

-Hal


Asking about the MC cable with 0-10v and line voltage together....nad how that's allowed and the raceways is not, We've discussed that 1000 times? Really?
 