Direct burial conduit bodies

Status
Not open for further replies.

csoc64

Senior Member
Location
northeast
I need to run a raceway down the side of a building and penetrate a foundation below grade for an LB to enter the building. What are my options for direct burial conduit bodies? RMC, PVC, etc. I am having a hard time finding any reference to conduit bodies that are listed for direct burial.
 
314.29 Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible.
Exception: Listed boxes and handhole enclosures shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation
 