R Rizz New member May 23, 2010 #1 Any one know what the burial depth for fiber is? Just under the lawn, not under a slab or driveway or anything. Iv lookd in 770 but didnt find much.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 23, 2010 #2 Wouldn't T.300.5 apply? I don't know for sure.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician May 24, 2010 #3 Per 770.3, 300.5 does not apply to optical fiber cable. The burial depth is a design issue and not a code issue for fiber.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 24, 2010 #4 don_resqcapt19 said: Per 770.3, 300.5 does not apply to optical fiber cable. The burial depth is a design issue and not a code issue for fiber. Click to expand... I didn't think 330.5 applied but I couldn't find anything else for depth. You are correct in that Art. 770.3 states that art. 300 applies only where it is referenced in art. 770. I misread that part and thought all of chapter 300 applied. Thanks for the correction.