Re: Directional Overcurrent Relay
Originally posted by oliver100:
also... i'm intrigued the differential relaying that was mentioned... An application was mentioned, but what is the BASIC function of diff. relays?
Differntial relay protection protects power plant generator from outside faults.
Actually, differential current relays only protect for faults inside of their zone and cannot protect a generator from external faults. But, a power system with differential current relays will have fast fault clearing times and that is always better for a generator.
A typical differential relay has two sets of current transformer inputs. The area between the two CT locations is the protected zone. The relay compares current into the zone with current out of the zone and trips if the currents don't match. The relays have adjustments to account for the different current values if the CT's are at different voltage levels or differnt ratios, such as when protecting a transformer with CT?s on the high and low voltage sides.
A differential current relay can have multiple CT inputs. An example is a switchgear bus differential relay that compares the main breaker current with the currents in all of the feeder breakers. It trips if all current going in is not coming out.
Differential relays provide the fastest response to faults. But the cost of the relay and CT's required usually restricts their use to larger generators and transformers (>5 MVA) or critical bus and switchgear.
On a generator, the differential CT?s are on the neutral leads (before the three phases are joined together on the neutral) and on the load side of the generator breaker. Faults in the generator or generator cables trip the unit immediately. A power system fault or a fault external to the generator is not detected.
Directional power relays protect a generator or utility from reverse power.