Not sure if this is the right place to post this. If I have a 'standard' 3 phase diesel genset with a 12 wire alternator and its accompanying AVR, is it possible to disable the alternator's output simply by interrupting the excitation circuit?
I have a couple rental units where the output is always live if the breaker is on, this has been a problem when a customer has run it out of fuel, or shut it down under load, as the voltage and frequency drop along with the engine speed. Looking into how I can retrofit these units to be like the other ones that have the load shut off (without using a contactor) by the controller. The controller on the units in question supports what I am looking to do so I don't need help there, just with the how to kill the alternator output portion.
I have a couple rental units where the output is always live if the breaker is on, this has been a problem when a customer has run it out of fuel, or shut it down under load, as the voltage and frequency drop along with the engine speed. Looking into how I can retrofit these units to be like the other ones that have the load shut off (without using a contactor) by the controller. The controller on the units in question supports what I am looking to do so I don't need help there, just with the how to kill the alternator output portion.