Disabling instantaneous protection possible while protecting switchboard?

Magic Gorge

Member
Location
Lexington, KY
For a selective coordination scheme, I am considering turning off the instantaneous function for both main and feeder breakers in a switchboard. Switchboards in question are designed per UL 891, meaning a 3 cycle withstand rating. The breakers have a minimum short-time delay setting of 0.05 seconds, which corresponds to 3 cycles. So, under these conditions is it possible to disable the instantaneous while also protecting the switchboard?
 
For a selective coordination scheme, I am considering turning off the instantaneous function for both main and feeder breakers in a switchboard. Switchboards in question are designed per UL 891, meaning a 3 cycle withstand rating. The breakers have a minimum short-time delay setting of 0.05 seconds, which corresponds to 3 cycles. So, under these conditions is it possible to disable the instantaneous while also protecting the switchboard?
A breaker listed to UL 489 will have what is equivalent to an instantaneous override point which means the Inst function is never completely removed. So, a properly sized UL489 breaker will always protect a UL891 switchboard.

However, you should consider the Arc Flash implications of removing the Inst function. At the least you may want to include an Arc Flash Incident Energy reduction switch.
 
A breaker listed to UL 489 will have what is equivalent to an instantaneous override point which means the Inst function is never completely removed. So, a properly sized UL489 breaker will always protect a UL891 switchboard.

However, you should consider the Arc Flash implications of removing the Inst function. At the least you may want to include an Arc Flash Incident Energy reduction switch.
Correct.
Besides, I don’t think you can fully disable the instantaneous trip of an MCCB listed to UL 489, it’s part of the listing of the breaker because that also protects the breaker itself from excessive current (up to the IC rating). In fact when you buy a UL 489 listed Molded Case Switch, which supposedly has no trips in it at all, it STILL has an instantaneous trip that is factory set for 10x the rated current of the device and 0.05sec. You can’t see it or adjust it on most brands, but it’s in there because UL requires it.
 
A breaker listed to UL 489 will have what is equivalent to an instantaneous override point which means the Inst function is never completely removed. So, a properly sized UL489 breaker will always protect a UL891 switchboard.

However, you should consider the Arc Flash implications of removing the Inst function. At the least you may want to include an Arc Flash Incident Energy reduction switch.
What if the available fault current is less than the override value? Say 50kA and override at 65kA. So the curve would look like short time pickup at 0.05 sec but the override never picks up. There are ARMS settings tabulated separately for maintenance mode.
 