electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
Ok well the title says it all, but i wanted to get some feed back here first since i generally assume i have overlooked something rather than the inspector being wrong. Single family residence, service entrance conductors enter a J/pull box and are tapped, to feed a 100A disconnect and a 200A service panel which are connected to the box with short runs of conduit, metal nipple to the 100A, pvc to 200A. I bolted a set screw terminal bar to the inside of the j-box, removing the paint under it first, and connected the three neutrals (feed and two taps) and the #2 grounding electrode conductor. To the same bar i also attached a bonding jumper to a bonding bushing on the rigid nipple that connects the j-box to the 100A disco. That is the layout and the inspecter cited two violations as follows:
"NEC 250.24 - an unspliced GEC shall land on the neutral buss in the service disconnect or disconnnects."
and
"NEC 250.6 - Parallel paths with the neutral conductor shall not be created."
Regarding thge first one, I see nothing in that section that states that i have to bring the GEC to the disconnects?
Regarding the parallel paths, he is referring to current being able to flow from from the neural buss in the 100A disco, thru the main bonding jumper (green screw), to the disco inclosure, thru the nipple, thru the j-box enclosure and/or bonding jumper, and to the neutral bar. I dont necessarily dispute that that is a parallel path, but what about exhibit 250.12 in the handbook, its the exact same thing? I know the handbook exhibits arent code but.....isn't this type of parallel path common in service equipment consisting of several enclosures?
Thanks in advance everyone
and