malachi constant
- Minneapolis
We are installing a new chiller to an existing facility. A couple things going on here:
1. When upgrading the utility transformer/connection cabinet, the customer would like to replace the CC with a custom combo CC/manual transfer switch. The intent of the transfer switch is to allow the entire facility - chiller and existing service - to be fed by a portable generator during an emergency.
2. To keep us from having to modify the existing service we want to feed the chiller direct from the transformer/conn cab/MTS.
I'm having trouble getting my head around the one line...
a) I assume a service disconnect is required ahead of the MTS (on the utility/line side) rated for both chiller and existing service combined. (In this case around 2000A.)
b) If I was doing this without the chiller - i.e. just feeding the service gear via the MTS - I would only need the disconnect noted above. But if that MTS/portable generator is to also feed the chiller, do I need to add two more disconnects, this time on the load side of the MTS, one for the chiller and one for the main service?
c) If the load side disconnects are required I would consider asking the customer to remove the chiller from the transfer switch. It would still be fed direct from the "connection cabinet" portion of the CC/MTS. Would this need a disconnect at the CC? I am thinking no, provided you put a disconnect at the chiller itself - if you took the MTS out of the equation, this (chiller directly fed from CC w/ no disconnect) is a code-compliant and fairly standard installation.
Other pertinent information:
* The run from CC/MTS to service equipment will be about 80', same for CC/MTS -> chiller.
* The chiller is located outside. It is around the corner in an enclosure, so would have a disconnect located at the unit. Tapping off the line side of the transfer switch without a disconnect there would not damage the chiller or transfer switch - only the unprotected exterior underground feeder. I suppose you could argue if the feeder melted it could take out the other equipment. I'm not really sure what code has to say about this.
* I plan to discuss with the electrical inspector, and the custom gear manufacturer, to get their thoughts, but would appreciate any insight you folks have.
Confusing situation. If a riser would help I can sketch one out and post it - let me know. Thanks!