Tim B.
Member
- Location
- Spokane Wa
Probably not going to run off of 120V.
Will probably need to cut the plug off and install a 240V plug.
That being said, a 240/230 motor chart shows 12 amps for 2 HP @ 240 volt!!!
6 amps at 240V for single phase is good for 3/4 HP.
Best check that sander for "CoronaVirus".
Pun intended?Horsepower ratings of . . . small air compressors are notoriously inflated.
Yet another example of the SI (metric) system eliminating confusion before it starts:
In the SI system, there's only one unit of power (the watt) and it would be plainly obvious that the 1492 watts of power coming out of the motor is more than the (hypothetical maximum) 1452 watts of power going in.
Look at the top center of the pic in the OP.Are you sure it is a 120 volt plug?
Agreed. The I in SI stands for international.Yet another example of the SI (metric) system eliminating confusion before it starts:
In the SI system, there's only one unit of power (the watt) and it would be plainly obvious that the 1492 watts of power coming out of the motor is more than the (hypothetical maximum) 1452 watts of power going in.
Sure, nice and clear.... With watts and HP, it is OBVIOUS the HP is work done and watts are power in. Lots clearer to me!![]()
The picture of the terminal block wiring shows that there's a jumper between U1 and V1. There is likely to be a first motor winding between terminals U1 and U2, and a second winding between V1 and V2. They are jumpered in parallel to allow operation at 110V. Verify that the jumper at the right of your picture goes between U2 and V2. I assume the black wire is connected via a switch to the hot and the white wire to neutral of the 120V input plug.Just received delivery of a new disc sander. It is a 1 Phase 220 Volt as you can see in the picture. The plug appears to be a standard 120 Volt household plug. Am i missing something? Thanks for any insight.
Nope. It is a RATE of doing work. Important distinction.With watts and HP, it is OBVIOUS the HP is work done
I looked at the picture, why did I not see it the first time?Look at the top center of the pic in the OP.
Indicative of a reseller who doesn't give a damn... The plug in that picture is a NEMA 5-15, which would be for 120V 15A max. The nameplate is showing 220V but the Amps are incorrect for a 2HP motor. So yeah, this is messed up all around, you just don't know where the mistake is (or mistakes are). So it's going to be up to you to sort it all out;Just received delivery of a new disc sander. It is a 1 Phase 220 Volt as you can see in the picture. The plug appears to be a standard 120 Volt household plug. Am i missing something? Thanks for any insight.