I am reducing line voltage (247 to 230 volts 1p) for an autoclave at a veterinary office. I do not see that a disco is required at the autotransformer (450.4) or am I incorrect? Aside from the NEC, does OSHA require a disco? The autoclave unit is plug and cord so no issue there 422.33. If no disco is the correct answer, then may I ask why? It seems to me a lock out device in a commercial application is the way to go. (we use 2008 NEC here)
thanks!!
 
450.14 Disconnecting Means.
Transformers, other than Class 2 or Class 3 transformers, shall have a disconnecting means located either in sight of the transformer or in a remote location. Where located in a remote location, the disconnecting means shall be lockable in accordance with 110.25, and its location shall be field marked on the transformer.

I believe this applies to all transformers including an autotransformer (which is what a buck - boost is), with noted exception of class 2 or 3 transformers.
 
Hello all,
I am reducing line voltage (247 to 230 volts 1p) for an autoclave at a veterinary office. I do not see that a disco is required at the autotransformer (450.4) or am I incorrect? Aside from the NEC, does OSHA require a disco? The autoclave unit is plug and cord so no issue there 422.33. If no disco is the correct answer, then may I ask why? It seems to me a lock out device in a commercial application is the way to go. (we use 2008 NEC here)
thanks!!

IMO it is a transformer and requires a disconnecting means. As a practical matter this requirement should not be especially onerous. A breaker lockout bracket on the CB supplying power suffices for the disconnecting means required as long as you put a sign at the transformer saying where it is.

ETA: The disconnecting means requirement does not seem to appear in the 2008 version.
 