H hhsting Senior Member Location Glen bunie, md, us Occupation Junior plan reviewer Mar 6, 2021 #1 Cat6 inside conduit separate from power conduit going from inside building office to network card in outdoor electric sign require disconnect?
Cat6 inside conduit separate from power conduit going from inside building office to network card in outdoor electric sign require disconnect?
Buck Parrish Senior Member Location NC & IN Mar 6, 2021 #2 Yes, the sign does if that's what you're asking. 600.6 (A) 2 -3 Controller yes 600.6- .A -3 (2) Last edited: Mar 6, 2021
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Mar 6, 2021 #3 The data cable does not need a disco. BTW, that Cat 6 cable will need to be wet location cable or it will fail in short order.
The data cable does not need a disco. BTW, that Cat 6 cable will need to be wet location cable or it will fail in short order.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 6, 2021 #4 Is this the same question you have asked before? Last edited: Mar 6, 2021