Not just foreign systems. Other electrical must be considered also under specific conditions.
When I stated "...that it does it not intrude on the required dedicated space, see 110.26 (F) (1) (a)", I was not saying that it does, but that it could and needs to be considered. 110.26 has restrictions on even electrical equipment when it comes to what can be located in another piece of equipment's working space.
I was remembering an illustration in Mike Holt's Understanding the 2008 Code at 110.26 (A)(3) where a transformer was placed under a panel. I went back to 2008 where it used to state at 110.26 (A) (3) "OTHER equipment such as ...cabinets, panels, etc., can be located above the electrical equipment, but must not extend more than 6 inches into the equipment's working space". I don't know how far that disco extends into that space. It is not just talking about foreign systems but other electrical equipment.
I see now that I mistakenly thought that meant 6 inches from the wall. 2014 however is worded a little differently. It says the same thing but it made me realize that the intrusion into a work space does not begin at the back of the equipment but past its front.