jobuTupaki
Member
- Location
- California
- Occupation
- Electrical Engineer
I have to size the breaker and a fused disconnect for a vacuum pump at 480V - nameplate rating: 20 HP (which gives 27 full load current, using NEC Table 430.250 (2017 version))
The manufacturer recommends 50A fused disconnect and I am scrambling trying to figure out how that was calculated. See below for my thoughts.
Using 27 as FLC, this gives FLA = 27/1.25 = 21.6
For the disconnect sizes I am calculating doing the following: FLA*225% --> 21.6A*225% = 48.6A, giving us the 50A fused disconnect, and I am going up to the standard size of 60A.
From here, I would use a 50A breaker since FLA is 48.6A?
I feel like I am going crazy/making up calculations trying to sort this out. Motors have always been very confusing to me. If anyone has any insight at all it would be greatly appreciated.
The manufacturer recommends 50A fused disconnect and I am scrambling trying to figure out how that was calculated. See below for my thoughts.
Using 27 as FLC, this gives FLA = 27/1.25 = 21.6
For the disconnect sizes I am calculating doing the following: FLA*225% --> 21.6A*225% = 48.6A, giving us the 50A fused disconnect, and I am going up to the standard size of 60A.
From here, I would use a 50A breaker since FLA is 48.6A?