Disconnect at House?

Ken_S

Senior Member
Location
NJ
Occupation
Electrician
Given - Remote ground mounted array, micro inverters, disconnect and combiner panel at the array. Is a disconnect required to be installed at the house where the feeder conductors enter? I believe 225.31 would require a disconnect, however I'm questioning if it's needed. The feeder conductors would enter the rear of the home and be run to the front of the home to an exterior disconnect connected to the line side of the service.

2020 NEC
 
Not required at the point where the feeders from the PV system enter the house as long as the disconnect requirements in 690.13 are met. The disconnect at the POI will satisfy 225.31 since the PV system will shutdown on opening that disconnect and deenergize the feeder conductors.
 