can anyone tell me when is a disconnect required between meter can and the breaker panel. Is there a certain distance that determines this?
It is not specified in the NEC. See 230.70 (A)(1) above as Charlie posted. In my area it is a judgement call, but usually no more than 10 feet inside is acceptable.Originally posted by bulldog195169:
what length requires a disconnect?
No, it's not. Read 230.6.Originally posted by bulldog195169:
if the wire was in conduit in the attic i assume that would be an acceptable means of protection.
That is all that the NEC says on the subject.230.70(A)(1) Readily Accessible Location The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
I will try to lay it all out.Originally posted by bulldog195169:
final try. does the nec state in any section that a disconnect must be connected between the meter can and the breaker panel if the wire does not go directly from the meter can into the panel. regardless of distance other than the wall penetration yes or no.
So conductors can be considered outside even if there are inside.230.6 Conductors Considered Outside the Building.
Conductors shall be considered outside of a building or other structure under any of the following conditions:
(1)Where installed under not less than 50 mm (2 in.) of concrete beneath a building or other structure
(2)Where installed within a building or other structure in a raceway that is encased in concrete or brick not less than 50 mm (2 in.) thick
(3)Where installed in any vault that meets the construction requirements of Article 450, Part III
(4)Where installed in conduit and under not less than 450 mm (18 in.) of earth beneath a building or other structure
As you have found there is no measurement, in my area about 5' is allowed.230.70(A) (1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
Hope this helps.No maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this Code has the responsibility for, and is charged with, making the decision as to how far inside the building the service-entrance conductors are allowed to travel to the main disconnecting means. The length of service-entrance conductors should be kept to a minimum inside buildings, because power utilities provide limited overcurrent protection and, in the event of a fault, the service conductors could ignite nearby combustible materials.
Some local jurisdictions have ordinances that allow service-entrance conductors to run within the building up to a specified length to terminate at the disconnecting means. The authority having jurisdiction may permit service conductors to bypass fuel storage tanks or gas meters and the like, permitting the service disconnecting means to be located in a readily accessible location. However, if the authority judges the distance as being excessive, the disconnecting means may be required to be located on the outside of the building or near the building at a readily accessible location that is not necessarily nearest the point of entrance of the conductors. See also 230.6 and Exhibit 230.15 for conductors considered to be outside a building.
I was thinking the same thing.Originally posted by charlie:
Bulldog (appropriate name),![]()
Is that your final answer?Originally posted by charlie:
Bulldog (appropriate name), no. Please see my first answer.![]()