For a 208V 3-phase automation control panel with 120V 1-phase loads connected between line and neutral, can a UL98 fusible disconnect be used as the main disconnect? The loads would be connected line to neutral without a transformer and therefore I was thinking 210.4(B) for MWBC would apply. All three phases would still be disconnected if you manually shut off the disconnect, but if a fuse blew, you could still have two live phases. I guess the other option would be to use a UL489 MCCB but this seems overkill for this small of a panel.
In the past, we typically have 480V 3-phase panels with a 1-phase transformer for our 120V loads.