Disconnect for 208V 3-phase automation control panel with 120v 1-phase loads

kloc5

Member
Location
United States
Occupation
Controls Manager
For a 208V 3-phase automation control panel with 120V 1-phase loads connected between line and neutral, can a UL98 fusible disconnect be used as the main disconnect? The loads would be connected line to neutral without a transformer and therefore I was thinking 210.4(B) for MWBC would apply. All three phases would still be disconnected if you manually shut off the disconnect, but if a fuse blew, you could still have two live phases. I guess the other option would be to use a UL489 MCCB but this seems overkill for this small of a panel.

In the past, we typically have 480V 3-phase panels with a 1-phase transformer for our 120V loads.

Thanks!
 

coop3339

Senior Member
Location
NJ
I'm not sure I follow completely but as long as you are using the correct size conductors and overcurrent protection with nothing exceeding its limits and all is listed for the use you should be okay.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Overcurrent protective devices are not required to open all 'live' conductors at the same time.

Disconnecting devices are typically required to open all of the live conductors.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
If any of the 120V circuits are for motor control I believe 430.75 requires all control circuits to be disconnected when the disconnect is open so you'd have a 4-pole disconnect. We had a recent related thread here:
 