Disconnect for hot tub question

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Can a breaker in site of the hot tub, be considered a disconnect? 680.12 says to disconnect all ungrounded conductors, and to be within site. Thank you for your help.
 

Smart $

Esteemed Member
Location
Ohio
Can a breaker in site of the hot tub, be considered a disconnect? 680.12 says to disconnect all ungrounded conductors, and to be within site. Thank you for your help.

(IMO) Yes, as long as it is between 5 to 50 feet away from water's edge and readily accessible.
 

bth0mas20

Senior Member
Location
Maryland
as long as the breaker is designed to disconnect all ungrounded conductors.....such as 2 pole if its 240v or single pole if its 120v.
 