Disconnect for Instahot

Status
Not open for further replies.

nvcape

Senior Member
We end up with lots of instant hot water heaters under the cabinets. The latest one is 60A, 208V. NEC 422.31(B) requires a disconnect for permanently wired appliances. As a 60A disconnect does't always fit in, the only option I know of is a locking device on the circuit breaker. Any ideas?
 

kelley

Member
Location
Massachusetts
Occupation
Estimator
Re: Disconnect for Instahot

I know that u said permanently wired, but how about making up a twist lock recepatcle set up? :)
 

tonyi

Senior Member
Re: Disconnect for Instahot

Originally posted by nvcape:
We end up with lots of instant hot water heaters under the cabinets. The latest one is 60A, 208V. NEC 422.31(B) requires a disconnect for permanently wired appliances. As a 60A disconnect does't always fit in, the only option I know of is a locking device on the circuit breaker. Any ideas?
You can only use the breaker if its within sight of the unit being served - not too many panels will be in this position...

How about putting a pullout on the wall next to the panel. This sort of unit doesn't appear to have an explicit disconnect location requirement like an A/C would.
 

nvcape

Senior Member
Re: Disconnect for Instahot

Kelly: 422.16 permits cords where the appliance is for "ready removal." These things are plumbed, so not sure can use a cord; will need to check further.
Tonyi: Code says you can have a remote switch or breaker if it can be locked open; still think this may be least cost and least problem.
 

tonyi

Senior Member
Re: Disconnect for Instahot

Originally posted by nvcape:
Kelly: 422.16 permits cords where the appliance is for "ready removal." These things are plumbed, so not sure can use a cord; will need to check further.
Tonyi: Code says you can have a remote switch or breaker if it can be locked open; still think this may be least cost and least problem.
An Idesco (somewhat)universal 2-pole lockout looks to be about the same price as a C/H unfused 60A pullout, maybe a dollar difference or so. I'd bet there's a lot better chance of a service guy actually using the pullout disco than a lockout ;)

With the 60A pullout, there's only one thing you have to stock because you know its compatible with everything being an external unit. The supposed universal lockouts really aren't - QO's, FPE's(ugh!) are all gonna be different than the GE/Murray/BR format breakers.
 