B bwyllie Senior Member Location MA Aug 19, 2003 #1 If a transformer is located in another room from where the primary is fed from, is a disconnect required by Code or just for safety? I cannot recall if there is a section of the code that requires this. Thanks
If a transformer is located in another room from where the primary is fed from, is a disconnect required by Code or just for safety? I cannot recall if there is a section of the code that requires this. Thanks
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 19, 2003 #2 Re: Disconnect for Primary of transformer The NEC does not require a local disconnect for a transformer. Primary OCPD is required, but that does not have to be at the transformer. Don
Re: Disconnect for Primary of transformer The NEC does not require a local disconnect for a transformer. Primary OCPD is required, but that does not have to be at the transformer. Don
B bwyllie Senior Member Location MA Aug 20, 2003 #3 Re: Disconnect for Primary of transformer thanks.