pault587
Member
- Location
- Grand Rapids, MI
I have two 25HP 460/60/3 motors that running pumps and being controlled by a VFD. Both pumps will operate at the size time. What size should the disconnect be?
Paul
Paul
As per 430.250 each motor has a FLA of 34A.pault587 said:I have two 25HP 460/60/3 motors that running pumps and being controlled by a VFD. Both pumps will operate at the size time. What size should the disconnect be?
Paul
I have two 25HP 460/60/3 motors that running pumps and being controlled by a VFD. Both pumps will operate at the size time. What size should the disconnect be?
KIRKBRO said:So if your motor is out of sight, code requires a disconnect,is there a exception, or one in the works .or how do you get around it???
pault587 said:When does the locked rotor amps come into the sizing of the disconnect? I think it was table 430.151 but I don't have the NEC with me right now. To clarify, there is one disconnect feeding both VFDs.
justdavemamm said:if the disc is before the VFD. Note that the OP did not tell the size of the VFD. It is common to have a vfd that is larger than the motor, so the rated input current is what I calculate from, not the motor amps.