So I'd check the nameplate and make sure that's the correct wattage.So in theory I could have
80A breaker @ 150% of the 51A,
#6thhn @ 125% for the conductors
With a 60A disconnect
Doesn't 422.11(F)(1) restrict branch circuit heater appliance loads > 48A to a 60A breaker?So in theory I could have
80A breaker @ 150% of the 51A,
#6thhn @ 125% for the conductors
With a 60A disconnect
Doesn't 422.11(F)(1) restrict branch circuit heater appliance loads > 48A to a 60A breaker?
Especially, since branch circuit rating is the same as supplementary OCPD, with interlocked heating elements that prevent operating together.
I believe the panel has an existing 70A breaker I could use. I would just need the non fused disconnect. I'm assuming a 100A since the 125% would put me over for a 60A disconnect.I've presented this similar scenario for plan check and it passed fine. On yours I'd submit ..
12300 / 240 = 51.25 x 125% = 64.06A
70 Amp breaker and 70A slow blow fused disconnect if possible with a #6 THHN or #4 if its over 100ft.