Is it a violation to fuse one pole of a 3 phase supply at a different amperage?If yes, could you please direct me to the pertinent code that would apply.
Is it a violation to fuse one pole of a 3 phase supply at a different amperage?If yes, could you please direct me to the pertinent code that would apply.
Are you feeding separate single phase loads? If so, and you have sized the disconnect for the highest load, sized the conductors appropriately, and you are OK with disconnecting all loads if needing to disconnect one of them, then there is no code issue I can think of.
If feeding a three phase plus a single phase from the same switch, I think it could be done if you paid enough attention to all of the details such as properly sizing the disconnect and ensuring that the lugs are rated for more than one conductor, and that the fuse sizes fit within the rules for both loads, but I think all of that will be highly unlikely.
If feeding just a three phase load, I don’t see the validity of even considering it.