Maybe.Originally posted by infinity:
Wouldn't a permanently installed breaker lock satisfy the requirement if the panel were more than 50' away or not within sight?
422.32 Disconnecting Means for Motor-Driven Appliance.
If a switch or circuit breaker serves as the disconnecting means for a permanently connected motor-driven appliance of more than 1/8 hp, it shall be located within sight from the motor controller and shall comply with Part IX of Article 430.
Exception: If a motor-driven appliance of more than 1/8 hp is provided with a unit switch that complies with 422.34(A), (B), (C), or (D), the switch or circuit breaker serving as the other disconnecting means shall be permitted to be out of sight from the motor controller.
Yes if you are sure the switch complies with 422.34 and the breaker with 422.34(D).Originally posted by jersey:
If these units have there own on/off then they can be hard wired right?
The key points;422.34 Unit Switch(es) as Disconnecting Means.
A unit switch(es) with a marked-off position that is a part of an appliance and disconnects all ungrounded conductors shall be permitted as the disconnecting means required by this article where other means for disconnection are provided in the following types of occupancies.
(D) Other Occupancies. In other occupancies, the branch-circuit switch or circuit breaker, where readily accessible for servicing of the appliance, shall be permitted as the other disconnecting means.
Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth.
If they didn't come with a cord and plug what did they come with?As far as installing a cord & making it plug & cord connected if the units did not come that way it maybe a violation of the UL listing.
It seems to me there is no UL listing violation for NOT using a plug and cord connection if the motor does not come that way.Originally posted by physis:
If they didn't come with a cord and plug what did they come with?As far as installing a cord & making it plug & cord connected if the units did not come that way it maybe a violation of the UL listing.
I've never heard of that. Why would cord and plug be a violation? The inspectors around here love when I install cord and twist locks on kitchen equipment.Originally posted by johndeereman:
As far as installing a cord & making it plug & cord connected if the units did not come that way it maybe a violation of the UL listing.
I'm talking about refrigerated units.Originally posted by physis:
If they didn't come with a cord and plug what did they come with?As far as installing a cord & making it plug & cord connected if the units did not come that way it maybe a violation of the UL listing.
By Bradleyelectric:
I'm talking about refrigerated units.