K KMeni Member Aug 25, 2008 #1 Are there any relate NEC code sections for Readily Accessable Disconnect Means for 480-208/120V 75KVA Transformer that is located 550' away from its main overcurrent protection for the primary conductors?
Are there any relate NEC code sections for Readily Accessable Disconnect Means for 480-208/120V 75KVA Transformer that is located 550' away from its main overcurrent protection for the primary conductors?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 25, 2008 #2 OCP has to be readily accessible (240.24) but not ncessarily any particular distance from the transformer. 5 ft or 550 ft makes no difference.
OCP has to be readily accessible (240.24) but not ncessarily any particular distance from the transformer. 5 ft or 550 ft makes no difference.