Disconnect Means for 75KVA Transformer.

Status
Not open for further replies.

KMeni

Member
Are there any relate NEC code sections for Readily Accessable Disconnect Means for 480-208/120V 75KVA Transformer that is located 550' away from its main overcurrent protection for the primary conductors?
 
OCP has to be readily accessible (240.24) but not ncessarily any particular distance from the transformer. 5 ft or 550 ft makes no difference.
 