Disconnect means for a transformer

Status
Not open for further replies.

herndon

Member
Does anyone know if I have a 75KVA(480v. 3p. to 120/208v. 3p.) step down transformer in a different room from the primary overcurrent protection.

Do I have to have a disconnecting means at the transformer for servicing it?

Thanks....
 

kripton

Member
Re: Disconnect means for a transformer

I believe you need a disconnect on the primary side only since it's a step down.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Disconnect means for a transformer

The NEC does not require either primay or secondary disconnects for transformers. Overcurrent protection is required for the primary, but is not required to be located at the transformer.
Don
 

pierre

Senior Member
Re: Disconnect means for a transformer

Article 450 covers protection of the transformer, Article 240 covers protection of the conductors.
For the transformer mentioned, table 450.3(B) is the reference for protection of the transformer.
408.16(D) will provide one with the info on the secondary side of the transformer for the protection of the panel on the secondary side.

Pierre
 

herndon

Member
Re: Disconnect means for a transformer

What I was looking for, is am I required to have a disconnecting means in sight of the transformer? For protection if I'm working on it...
 

gregory

Senior Member
Re: Disconnect means for a transformer

240.40 Disconnecting Means for Fuses.
A disconnecting means shall be provided on the supply side of all fuses in circuits over 150 volts to ground and cartridge fuses in circuits of any voltage where accessible to other than qualified persons.

If you have fuses protecting the transformer primary and it is 277 volts,(over 150 volts to ground) you must have a disconnect for the fuses that protect the primary.
 