I have a piece of permanent equipment (3 hp-480V motor) that came with a male 480V 20A twist lock cord cap. Can I feed the motor with a cord drop from the ceiling with a female 480V 20A cord cap and use them has a disconnect means? I have done it years ago in different plants, but just not sure now. Thank you
 
Cord Cap

Cord Cap

The cord cap can be used as a disconnecting means if it is listed as such. Make sure you look at 400.5 for the cord ampacity requirements - we use #10 SO cord for 20A cord drops here.

Cords aren't permitted for permanent equipment, so it would be best to ask the AHJ what "permanent" is in his mind.

Also, see 368.56 (B) for cord drops from busways.
 