I think I did this emergency job today right, but I'm still not sure. It passed inspection, but I've come to believe that many things pass inspection that don't exactly square with the NEC...
Building was fed from a downtown network secondary into the basement of the building. 208V, single phase. The secondary conductors first hit an existing 400 amp disconnect, which contained the main bonding jumper and the grounding electrode terminations. From there, two 200 amp subfeeds split off to two seperate 200 amp disconnects. No metering involved thus far. The load side of the one 200 amp disconnect is where my work was being done. This 200 amp feeder went to 6 old A base tennant meters and 6 old fuse panels. The thing went down in a blaze of glory.
Here's what I did... I ran 200 amp subfeed cable from the existing 200 amp disconnect to a 6 gang meter socket. I landed the both hots and the neutral on the ganged meter socket line side as usual. I landed the EGC of the subfeed on a distribution block that I mounted in the ganged meter socket (tons of extra room). From the load side of each meter gang, I ran 100 amp subfeed cable to each of 6 panels directly below the meter socket, naturally with neturals and grounds on seperate bars in each tennant panel. The EGC of each load side cable terminated on that distribution block I mounted in the meter can.
What I'm puzzled about is the arrangement I came up with in the ganged meter socket for keeping this neutral and ground seperate, since this socket was after the main disconnect. Is this normal? That is to say, is this how most people do it? I know it's a bit rare to have the metering being done on the load side of a main disconnect when there isn't a factory type meter stack involved. I just want a double check with smart people for the next time I bump into this. I am so famaliar to the inspectors that they hardly check my work, which isn't always what I want.
Thanks.
Building was fed from a downtown network secondary into the basement of the building. 208V, single phase. The secondary conductors first hit an existing 400 amp disconnect, which contained the main bonding jumper and the grounding electrode terminations. From there, two 200 amp subfeeds split off to two seperate 200 amp disconnects. No metering involved thus far. The load side of the one 200 amp disconnect is where my work was being done. This 200 amp feeder went to 6 old A base tennant meters and 6 old fuse panels. The thing went down in a blaze of glory.
Here's what I did... I ran 200 amp subfeed cable from the existing 200 amp disconnect to a 6 gang meter socket. I landed the both hots and the neutral on the ganged meter socket line side as usual. I landed the EGC of the subfeed on a distribution block that I mounted in the ganged meter socket (tons of extra room). From the load side of each meter gang, I ran 100 amp subfeed cable to each of 6 panels directly below the meter socket, naturally with neturals and grounds on seperate bars in each tennant panel. The EGC of each load side cable terminated on that distribution block I mounted in the meter can.
What I'm puzzled about is the arrangement I came up with in the ganged meter socket for keeping this neutral and ground seperate, since this socket was after the main disconnect. Is this normal? That is to say, is this how most people do it? I know it's a bit rare to have the metering being done on the load side of a main disconnect when there isn't a factory type meter stack involved. I just want a double check with smart people for the next time I bump into this. I am so famaliar to the inspectors that they hardly check my work, which isn't always what I want.