I've come to a point were I need some help on a clubhouse project. I'm the EE on this project. 208V, three phase system, 1400A. We had the transformer pad close to the building and disconnect installed right outside the building. The MDP was MLO 30 ft inside the building. One of the owners dropped in to take a look and said the transformer and disconnect must be moved.
Architect and EC have worked with POCO to move the transformer and disconnect to a new location about 230 feet away from building. All conductors underground.
My question is about where the bonding jumper between the neutral and ground should happen in the new arrangement. Originally I landed the GEC in the outside disconnect and ran a ground conductor (with the phase conductors & neutral) from the SD to the MDP.
With the service disconnect so far away, I want to treat the conductors from the disconnect to the MDP as if they were service entrance conductors. Can I do this and not install a ground conductor with the phase conductors? IE only phase conductors and neutral.
The GEC will have to be landed in the MDP now. It doesn't make sense to me to run ground conductors between the Service Disconnect in this instance, but I can't find an exception in the code that will allow me not to.
Does anyone see the fallacy in my thinking?
Architect and EC have worked with POCO to move the transformer and disconnect to a new location about 230 feet away from building. All conductors underground.
My question is about where the bonding jumper between the neutral and ground should happen in the new arrangement. Originally I landed the GEC in the outside disconnect and ran a ground conductor (with the phase conductors & neutral) from the SD to the MDP.
With the service disconnect so far away, I want to treat the conductors from the disconnect to the MDP as if they were service entrance conductors. Can I do this and not install a ground conductor with the phase conductors? IE only phase conductors and neutral.
The GEC will have to be landed in the MDP now. It doesn't make sense to me to run ground conductors between the Service Disconnect in this instance, but I can't find an exception in the code that will allow me not to.
Does anyone see the fallacy in my thinking?