COLD SEQUENCE METERING
The use of line-side disconnects may be required by the Company or the local Public Authority. Line-side disconnectsshall be installed on the same wall directly ahead of and within 24" of the meter.
The cold sequence disconnect(s) shall contain provisions for a Company wire seal for the cover and a Company padlock in the operating handle lock-off position. Wire seals will be used by the Company to secure the enclosure from unauthorized entry and will allow the customer emergency access to reset breakers or to replace fuses. A Company padlock will only be used to lock disconnects in the off position for services that are shut off.
The amp rating of the cold sequence disconnect shall not exceed the amp rating of the meter socket and shall be installed in accordance with 2002 NEC? Article 230, or as may be amended.
The cold-sequence disconnect on a 3-phase, 3-wire, corner -grounded delta service shall be a 2-pole device and the grounded phase shall not be switched. The grounded phase shall not be fused in accordance with 2002 NEC? Article 230.90(B), or as may be amended.
The cold sequence disconnect(s) shall be furnished, owned, and maintained by the customer.
Cold-sequence metering will only be required on commercial and industrial self-contained meter installations for 480 volt services, for both single -phase and three-phase. In addition, no current-limiting fuses will be required for any services, inclusive of 480 volt and below. With regard to 480 volt services, the cold-sequence disconnect may be a circuit breaker, molded case circuit switch, T-type Pullout, or a non-fusible load-break safety switch. The disconnect shall be rated load-make/load-break and shall be capable of being operated and maintained without opening the enclosure. All affected services shall have the disconnect operating handle accessible to the customer without opening the enclosure cover. Multiple tenant meter sockets are permitted to have a single currentlimiting main disconnect ahead of the common bus. Local Public Authorities may not allow overcurrent protection devices ahead of the electric meter. Please check with your local Public Authority to determine requirements relevant to overcurrent protection.