iggy2
Senior Member
- Location
- NEw England
We are designing a lab for a client. Wall panels are modular, and have flush outlet boxes in the panel, with emt from the box stubbed to the top of the wall panel. Some of the outlet boxes will serve a disconnect, some will serve receptacles in surface wiremold.
Can a disconnect, or G4000 wiremold be mounted over (covering) the outlet box, if the wires are not spliced in the outlet box? Or would access be required to the outlet box without having to remove the wiremold or the disconnect?
314.29 says "boxes" (not specific to outlet, pull or junction...) have to be accessible without removing any "part of the building or structure". the disconnect, or the wiremold is not "part of the building"... I assume by 'building' they mean wallboard, studs, beams, concrete, floors, etc.
Thanks.
Can a disconnect, or G4000 wiremold be mounted over (covering) the outlet box, if the wires are not spliced in the outlet box? Or would access be required to the outlet box without having to remove the wiremold or the disconnect?
314.29 says "boxes" (not specific to outlet, pull or junction...) have to be accessible without removing any "part of the building or structure". the disconnect, or the wiremold is not "part of the building"... I assume by 'building' they mean wallboard, studs, beams, concrete, floors, etc.
Thanks.