Disconnect required for each pole for sports field lighting?

Status
Not open for further replies.

Kenneth Smith

New member
Location
Madison, Va
Does the 2011 NEC require a separate disconnect for each pole light for a softball field. 6 lights on each pole with 1500 Watt Metal halide bulbs. Do the breakers in the distribution panel that feeds these poles need to be HID rated?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Does the 2011 NEC require a separate disconnect for each pole light for a softball field. 6 lights on each pole with 1500 Watt Metal halide bulbs. Do the breakers in the distribution panel that feeds these poles need to be HID rated?

Take a look at 225.32 exception #3.

If you are using the CB as light switches, I would say the answer is yes.
 