Heater nameplate indicates 12kw 240v 1ph, 52FLA, suggested wire size #6, Max Circuit Breaker 70 amp (which I plans on using)
In that case, shouldn't the wire size be #4, and, should the disconnect size for this be 60 amp? or 100 amp rated?
Planning on installing the disconnect within sight. Pipe and wire.
Thank You,
JAP>