430.110 Ampere Rating and Interrupting Capacity.
(A) General. The disconnecting means for motor circuits
rated 600 volts, nominal, or less shall have an ampere rating
not less than 115 percent of the full-load current rating
of the motor.
Exception: A listed unfused motor-circuit switch having a
horsepower rating not less than the motor horsepower shall
be permitted to have an ampere rating less than 115 percent
of the full-load current rating of the motor.