It is a single point power the MOCP is 450, but i am going to try to get by with the existing 400a breaker feeding it. Even if i change to a 450a breaker can i still use the 400a disconnect?
Disconnect switches are horsepower rated therefore have a maximum locked-rotor capability. Don't forget to check the locked-rotor current rating of the chiller unit.