Re: disconnect sizing
Originally posted by bond:
Thank you Bob for the info and more clear now but i think it would be a code violation
No it is not a code violation, that I am 100% sure of.
Take a look at 2002 NEC 240.4(G)
240.4(G) Overcurrent Protection for Specific Conductor Applications. Overcurrent protection for the specific conductors shall be permitted to be provided as referenced in Table 240.4(G).
I can not post table 240.4(G) but if you look at it one of the sections in the table is Air-conditioning and refrigeration equipment circuit conductors 440, Parts III, VI.
if i put a forty amp breaker for #10 thhn ,it does not protect my wire very well does it ?
Yes and no, it protects the wire against short circuits and ground faults, it does not protect the wire against overload, it is not required to for this application. The thermal overloads in the HVAC unit itself protect the conductors against overloads.
secondly i dont care who,how or why but I myself would never dream of putting a fuseless disconect on a unit whether on the roof or anywhere else because on such a long run back to a breaker arent we increasing impedence and increasing the ampacity in case of a fault so far away from the breaker? Isnt that why we put fused disconnects close to the unit ?
You are free to make that choice
but many people use non fused disconnects for this every day.
Yes the impedance increases but remember the breaker back at the panel is only there for short circuits and ground faults, it will take a heck of a long run before impedance becomes an issue under short circuit or ground fault conditions.
arent all breakers these days HACR rated so there is no nuisance tripping?
Yes I think you are right but regardless of that if the units tag only says maximum fuse size you must use a fuse, an HACR breaker will not meet code for a unit only marked with max fuse size.
Please check out the following thread, read BPHGravity's and Charlie's posts carefully, BPHGravity provides some more code references to this subject.
feeder to heating and air package unit
Bob
[ November 26, 2004, 02:57 PM: Message edited by: iwire ]