Disconnect Sizing

Status
Not open for further replies.

WastefulMiser

Senior Member
Location
ANSI World
Is it OK to size a disconnect at rated current v. what the OCPD is?

Ex:

75kva xfmr, 480P, 208Y/120S, the OCPD is located elsewhere for the primary and is sized for 250% rated primary current.

Is it OK to size the local disconnect 75000*1.15/480/1.7321?
 
Is it OK to size a disconnect at rated current v. what the OCPD is?

Ex:

75kva xfmr, 480P, 208Y/120S, the OCPD is located elsewhere for the primary and is sized for 250% rated primary current.

Is it OK to size the local disconnect 75000*1.15/480/1.7321?

Which Code cycle are you installing under, is the disconnect on the pri or sec?? and why are you installing it??
 
What size primary overcurrent protection and wire are you planning to use. You mentioned sizing it a 250% so it will be impossible to terminate this large of wire in a 100 amp disconnect.
 
What size primary overcurrent protection and wire are you planning to use. You mentioned sizing it a 250% so it will be impossible to terminate this large of wire in a 100 amp disconnect.

Thanks for the reply.

Ideally I guess 225A, so I believe that is a 4/0 without looking at the chart.

But you have a good point about the termination. I guess I should verify if 100A disconnect lugs can handle that size of a cable.
 