Is a one circuit 240 volt breaker disconnect installed down stream of the main disconnect considered a sub-panel.
A sub-panel isn't defined by the NEC what's the reason that you may need to define what it is?
If it was done before 1996 NEC applied it may have been OK. After then it at least needed a separate EGC.OK, here is what I saw in the basement of a resident the other day when I was troubleshooting another circuit.
A 100 amp SER, four wire was feeding a detached garage. This circuit was taped in the basement in a jbox. The tap run about 8 feet and ended in a disconnect with a thirty amp two pole breaker. The disconnect was fed with three wires from the jbox,, no egc. Thls disconnect fed a three wire clothes dryer receptacle.
It seem wrong to me.
It needed the separate EGC back then too....the only time you could omit the EGC for a dryer or range circuit was when the circuit originated at the service equipment.If it was done before 1996 NEC applied it may have been OK. After then it at least needed a separate EGC.
Not really certain if you could bond such a disconnecting means with the neutral back in those days, but it was done a lot when fuses were common instead of breakers.
It needed the separate EGC back then too....the only time you could omit the EGC for a dryer or range circuit was when the circuit originated at the service equipment.
The grounded conductor is insulated, or the grounded
conductor is uninsulated and part of a Type SE service-
entrance cable and the branch circuit originates at the
service equipment.
What about that rule using a insulated grounded conductor, did it apply then also?
I omitted the other qualifiers on purpose.
Yes that applied too.What about that rule using a insulated grounded conductor, did it apply then also?
I omitted the other qualifiers on purpose.
You are probably correct. Around here the only 4 wire range/dryer circuits you ever saw was in mobile or manufactured homes, until the 1996 NEC came out, service or feeder supplied panel didn't really matter. Three wire feeders to separate structures was also normal regardless of other conditions.It needed the separate EGC back then too....the only time you could omit the EGC for a dryer or range circuit was when the circuit originated at the service equipment.