Is a disconnect switch always needed on the secondary sideof a transformer per code?
That is the way it works out most of the timeOk the secondary side conductors are feeding a panel 200 feet away so disconnect is needed if I'm reading 1-6 correctly.
Ok the secondary side conductors are feeding a panel 200 feet away so disconnect is needed if I'm reading 1-6 correctly. Transformer is delta to wye
a disconnect is not required on the secondary side, however it often works out that it is a convenient place to put the OCPD that may be required.
you might also need it for other reasons, such as the disconnect feeding a separate structure.
But we are trying to determine if a mcb in the panel 200' away can serve as the means of disconnect. Some are saying not because of he distance away from the transformer.That is the way it works out most of the time
But we are trying to determine if a mcb in the panel 200' away can serve as the means of disconnect. Some are saying not because of he distance away from the transformer.
But we are trying to determine if a mcb in the panel 200' away can serve as the means of disconnect. Some are saying not because of he distance away from the transformer.
You need to have the OCPD with no more than 25' of the secondary conductor length so no 200' away won't work with a main in the panel.
The issue is not the disco itself but the overcurrent protection it provides for the wires.So the disco has to be within 25' of the transformer and not at the panel 200' away? Thx
what if it is outside?
Different scenario, is this installation outside?