Is it acceptable to supply a 30A,208V, 3 phase fused disconnect with a 60A,208V 3 phase circuit as long as the line side wiring is rated for 60A and the load side wiring is rated for 30A?
is this a fused disconnect?Is it acceptable to supply a 30A,208V, 3 phase fused disconnect with a 60A,208V 3 phase circuit as long as the line side wiring is rated for 60A and the load side wiring is rated for 30A?
The op states it is fused. What , may I ask, does that have to do with the question?is this a fused disconnect?
Is it acceptable to supply a 30A,208V, 3 phase fused disconnect with a 60A,208V 3 phase circuit as long as the line side wiring is rated for 60A and the load side wiring is rated for 30A?
is this a fused disconnect?
missed fused. What would your answer be if the 30 A disconnect was unfused?
Well if it were fused at the panel at 60 amps and not at the disco, we would have an issue with 30 amp wiring on the load side unless this was an a/c unit with max OCP at 60 and Minimum cir of 30-- not likely.missed fused. What would your answer be if the 30 A disconnect was unfused?
Well if it were fused at the panel at 60 amps and not at the disco, we would have an issue with 30 amp wiring on the load side unless this was an a/c unit with max OCP at 60 and Minimum cir of 30-- not likely.
If the 60 amp wiring was protected at 30 amps then the lugs may be an issue but the egc problem could be a bigger issue as I stated earlier.
didn't intend to hijack this thread. Sorry
If the op doesn't respond then it's fair game.What hijack? The OP was answered and I thought we were just talking about other related scenarios. I do not see that as a hijack.
Gus said::grin: we would still have a problem: 440.12
(1) Ampere Rating. The ampere rating shall be at least 115 percent of the nameplate rated-load current or branch-circuit selection current, whichever is greater.
(couldn't resist because it was you, Dennis) Today 09:04 AM