disconnect terms

Status
Not open for further replies.
I had a master elec. tell me to day that it's ok to term line on the load side as long as you lable it as such. I say he's load any thoughts?:roll:
 

480sparky

Senior Member
Location
Iowegia
If it's a fused disco, he's asking for a big shock when he goes to change the fuse.

Does this master say you can have 'reverse polarity' on a standard 120v receptacle as long as you label it?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Fuses must be on the load side of a disconnect.

Open switch blades must be de-energized when off, unless they are barriered.

Circuit breakers can be "reverse" fed unless they carry the specific markings identifying "line" and "load".
 
Status
Not open for further replies.