Disconnect to Panel

Status
Not open for further replies.

JRPME

Member
Location
Texas
Occupation
Project Manager
I have a location that has a direct feed to the transformer on the primary side and the secondary side feeds a 200A fusible disconnect. The panel for the job has 100MCB. Do the fuses in the disconnect need to be changed to 100A or are the 200A fuses ok?
 
Need to know how you are related to the electrical industry in your occupation.
And you are missing important information in your post
 
I am an electrician in Texas. I say the 200A fusible disconnect can feed the 100A MCB panel but I was told I couldn't.
 
The panel has to be protected at 100A. That can be done either with the Fused Disconnect or the main breaker in the panel itself.

The wiring between the 200A fused disconnect and the panel either has to be rated for 200A OR qualify under one of the tap rules for 100A. If you cannot do either, you need to fuse at whatever the feeder requires.
 