250V vs 600V Rated Disconnect Switches
250V vs 600V Rated Disconnect Switches
Eaton's 250 V disconnects are about 55% of the height and 80% of the width of their 600V line. There's a reason for that larger dimensions.
Phase-to-phase and phase-to-ground clearances and insulation will be different. There is a good chance of a flashover across the reduced dimensions when a voltage surge occurs.
The opening between the energized fixed part of the disconenct and the switch arm will be less at 250V. It might flash over when you think the load is disconnected.
If the disconnect is opened under load, the shorter travel of the moving part may not be enough to break the arc. That will lead to a flashover and an exploding enclosure.
If the switch is a fused style, it will not accept 600V fuses. When a fault occurs, the 250 V fuses will blow up. The arc could destroy the wire, the enclosure and initiate a fire. I investigated under rated fuses causing fires that took down whole MCC's in a government building.
Bottom line- not a good idea.