Jerry Morse
New member
First Time Poster here.....
We recently built a control panel for a customer and we need to correct something I believe I identified as not acceptable.
The incoming 120V power terminates on the line side of a class CC Fuseholder "FU1" (fused with a 15A fast blow / 200Kaic fuse) and a terminal block dedicated for the neutral. There is also a main ground lug dedicated for the incoming ground as well.
After the panel was completed; I noticed that the fuse holder states that it is not to be opened under load. I believe this is a problem. This fuse holder is our main disconnect for the panel and is located within the enclosure.
What are my options to correct?
A) Replace the 15 amp fuse holder with a UL489 Miniature Circuit Breaker (this is not our first choice due to space)...... or
B) Provide instructions on the drawings to have a disconnect installed by the end-user and for it to be rated at 15 amps?
Thanks,
AJ
We recently built a control panel for a customer and we need to correct something I believe I identified as not acceptable.
The incoming 120V power terminates on the line side of a class CC Fuseholder "FU1" (fused with a 15A fast blow / 200Kaic fuse) and a terminal block dedicated for the neutral. There is also a main ground lug dedicated for the incoming ground as well.
After the panel was completed; I noticed that the fuse holder states that it is not to be opened under load. I believe this is a problem. This fuse holder is our main disconnect for the panel and is located within the enclosure.
What are my options to correct?
A) Replace the 15 amp fuse holder with a UL489 Miniature Circuit Breaker (this is not our first choice due to space)...... or
B) Provide instructions on the drawings to have a disconnect installed by the end-user and for it to be rated at 15 amps?
Thanks,
AJ