Bryan-79
- Nampa idaho
- Electrician
Where in the nec can I find the 125%2023 NEC
The 80 % can't be found for the disconnect.
It's the reciprocal of 125% which is what the NEC uses for continuous duty.
Example: 1 / 1.25 = 0.8 or 80 %
Example : 1/ .80 = 1.25 %
Panelboard's and disconnects have that 80 % rating.
When we size our continuous loads the NEC requires 125% of the load, so that satisfies the '80 %' rule.
Make sense? Sure does, 'cause NEC says so.
Oh, I can't forget to say.......
Thanks for reading.
Comments accepted.
TX+MASTER #4544