I'm confused. What does the following mean: 60/2/40. This is fed from a 20A breaker.
I would normally take that to be the somewhat common shorthand some folks use to designate the disconnect, in this case 60-amp frame, 2-pole, 40-amp fuses.
However, if it's indeed fed from a 20-amp device, then I'm not so sure...
What is that printed on? A piece of equipment? Are you sure it is not 60/240-- which means 60 cycle 240VI'm confused. What does the following mean: 60/2/40. This is fed from a 20A breaker.
Fused disconnect: 60A Frame, 2 pole, 40A Fuses.On the drawing the disconnect is annotated as 60/2/40. I understand this to mean 60A rated disconnect, 2 Pole, 40 A fuses. But the OCPD on the panel schedule says 20A 3P Am I reading the disconnect annotation correctly? The load is a condenser.
Thanks a lot